Dale001289
Senior Member
- Location
- Georgia
We have a HRG @10A at a 81.250MVA steam generator (neutral grounding transformer 13.8kV/240V) and a LRG (resistor) @ 400A downstream from the generator at the 13.8kV switchgear bus.
One of our Leads is telling me fault current at any point on the grid - including EGC's - will be limited to 410A max due to the existence of these two impedance grounding systems. This include lightning strikes, ground faults to conduits, equipment, structural steel, cable tray i.e., at any point downstream from the two impedance grounds throughout the entire plant. I tried to explain, fault current is reduced only AFTER it passes through the impedance grounding systems - not before when fault current could be in the thousands of amps, such as a 100KA lightning strike to the electrode systems, such as steel tower or ground fault within a major piece of equipment.
This is very basic stuff - but how do I convince this guy he's wrong?
One of our Leads is telling me fault current at any point on the grid - including EGC's - will be limited to 410A max due to the existence of these two impedance grounding systems. This include lightning strikes, ground faults to conduits, equipment, structural steel, cable tray i.e., at any point downstream from the two impedance grounds throughout the entire plant. I tried to explain, fault current is reduced only AFTER it passes through the impedance grounding systems - not before when fault current could be in the thousands of amps, such as a 100KA lightning strike to the electrode systems, such as steel tower or ground fault within a major piece of equipment.