HSB 24 kw generator close to pool

Status
Not open for further replies.

patricknola

Electrical contractor/Generac Dealer
Location
new orleans, La, United States
Occupation
Electrical contractor.
Hey Guys, I've got a customer who wants a home standby generator. There is little space. He has his 2 a/c condensers and pool pumps approximately 10-15 feet from the pool, in the back yard. I could put the generator 5 feet fro. the a/c condensers and 7 feet from the pool. Does this sound nec compliant?
 
What code cycle?
If the 2020 maybe 680.22(E)
I’m reaching here…

680.22(E).
OtherEquipment.
Other equipment with ratings exceeding the low voltage contact limit shall be located at least 5ft horizontally from the inside walls of a pool unless separated from the pool by a solid fence, wall, or other permanent barrier. (Other equipment would include but not be limited to meter sockets, panels, disconnects, a/c units)
 