Hub Bushing
Alwayslearningelec
NJ
Estimator
So this has a locknut on it but no bushing. Is a sperate bushing required? I assume no beccasue it has an insulated throat?
Just be careful with the spec.
Often times the specs call for these hubs to be grounding type
It comes with a bonding locknut. You could also purchase the grounding locknuts separately.
You're correct that is spec most of the time. I believe it's a locknut with a screw on it
Nema 4x..why?
If it's stainless steel there's going to be a galvanic corrosion issue with the hub. We started switching to stainless steel hubs to prevent the issue.
However, if the design and specifications called for this, then that would become a design problem.
I think those would probably cost less too.
The issue would become protecting the threads at the hub. The SS hub will not have the protected sleeve that the one you showed does.
You will need approval if the specs do not specify the SS hub. They might accept a length of heave duty heat shrink over the hub and the first couple of inches of conduit.