Can some one tell me the requirements for a humidifier. A contractor mounted a 100 amp fused disconnect and the manual called for a enclosed circuit breaker. He said it is not code and left the fused disconect. There is water at the system and the non weatherproof disconnect is mounted under the 225 degree air and is within 3' of the unit. Does anyone have any info to help me with this please.
 
A contractor mounted a 100 amp fused disconnect and the manual called for a enclosed circuit breaker.

If the manufactures installation instructions are calling for a enclosed circuit breaker then it is a violation of 110.3(B) to install a fused disconnect.

Chris
 