AC\DC
Senior Member
- Location
- Florence,Oregon,Lane
- Occupation
- EC
I have a job that is associated with a previous post I made. I need help turned into something I was not expecting.
I was called for a 200 amp main tripping in a heated storage unite complex. They say it has been tripping for 3 months when the temps get in low 30’s. They wanted me to change the main out cause they thought it was going bad. I asked them if they added any new loads or if something has changed, they said no. I could not see if the breaker was overloaded when I was their. I was planning on popping out late at night when it got cold again.
I I told them you might be overloaded and will have to go to 400 amp. This complex’s has multiple services all 200amp 120/240. They insisted to just change breaker and it’s not overloaded.
I got the PO to come pull meter then we found the neutral almost blown apart.Main breaker was striped out. I jumped to the conclusion that this was the problem, at the time it made sense.
slaped a new 200 square d homeline meter main up last night. Got it powered up today. Flipped the breakers on and a humming noise starts. Every load came on, they sat all night with no power so they were all cold . Checked with my amp meter and it was reading 180 and bang main tripped.
I usually use CH but wanted to try square d.So the main breaker has 4 copper wires feeding the200 amp main. I can only get the clamp in between the end wires. phase a is drawing about 40 amps more than b. Though when I try and check the other phase a it only reads a fraction. Since it’s in the middle of the breker would it not read it correctly since i am not fully seating the wire and any cancelation from other phase. It feels warmer also. I am charging my thermal camera to check it out
Latter.
Is the humming i hear from the large load .if I turn any large load off it dies down a lot. The squad d panels allowed me to fish the conductors behind the panel so it looked neat and it would actually fit.
The meter main feeds three sub panels and a lot of their breakers and buss are correded.
My biggest concern is that that the 200 amp breaker wires got damaged somehow When I got my Conductors behind the panel. I checked when installing and the back side was completely smooth.
I left cause I need to think. I turned off a few heaters so they can atleast have lights. The connection to the main were not tourqed correctly from factory, I corrected. could I have a lose connection on my high reading a phase in the meter section?
Any help will be appreciated. Attached are some picture of the blown out panel and the new on
I was called for a 200 amp main tripping in a heated storage unite complex. They say it has been tripping for 3 months when the temps get in low 30’s. They wanted me to change the main out cause they thought it was going bad. I asked them if they added any new loads or if something has changed, they said no. I could not see if the breaker was overloaded when I was their. I was planning on popping out late at night when it got cold again.
I I told them you might be overloaded and will have to go to 400 amp. This complex’s has multiple services all 200amp 120/240. They insisted to just change breaker and it’s not overloaded.
I got the PO to come pull meter then we found the neutral almost blown apart.Main breaker was striped out. I jumped to the conclusion that this was the problem, at the time it made sense.
slaped a new 200 square d homeline meter main up last night. Got it powered up today. Flipped the breakers on and a humming noise starts. Every load came on, they sat all night with no power so they were all cold . Checked with my amp meter and it was reading 180 and bang main tripped.
I usually use CH but wanted to try square d.So the main breaker has 4 copper wires feeding the200 amp main. I can only get the clamp in between the end wires. phase a is drawing about 40 amps more than b. Though when I try and check the other phase a it only reads a fraction. Since it’s in the middle of the breker would it not read it correctly since i am not fully seating the wire and any cancelation from other phase. It feels warmer also. I am charging my thermal camera to check it out
Latter.
Is the humming i hear from the large load .if I turn any large load off it dies down a lot. The squad d panels allowed me to fish the conductors behind the panel so it looked neat and it would actually fit.
The meter main feeds three sub panels and a lot of their breakers and buss are correded.
My biggest concern is that that the 200 amp breaker wires got damaged somehow When I got my Conductors behind the panel. I checked when installing and the back side was completely smooth.
I left cause I need to think. I turned off a few heaters so they can atleast have lights. The connection to the main were not tourqed correctly from factory, I corrected. could I have a lose connection on my high reading a phase in the meter section?
Any help will be appreciated. Attached are some picture of the blown out panel and the new on