Branch circuit breaker supplying mainly or only lighting. Hmm. Considering the suggestions already been made... Does it only hum while load is applied? (I've had humming 200 A 3ph Square-D QO Main in a 40 space, even after all shutting off all breakers below, and was barely even acceptably warm to the feel -- next to an identical panel that was totally silent) If convenient narrow down to the problem being the breaker or the load sending back undesirable eddies by: 1) swapping the breaker 2) swapping the load to another breaker of same size in the same panel. 3) if the load causes a different breaker to hum, then the breaker isn't the issue, it is likely from the load. 4) load-test that breaker with a pure resistive load directly to the panel's neutral , will give an idea if it's an inductive circuit load issue. Even if a it's a brand new breaker, and you narrow the problem down to the breaker being the culprit, I have learned that "new" just means that you recently paid money for it, not that it couldn't be defective. If it's the circuit causing the hum, and if you can't physically see all the load, such as in an open warehouse, maybe there's more than meets the eye happening. Not knowing if it's a single or polyphase panel, something else could have been connected to the branch circuit by someone else at some period in the past, and perhaps there's a sharing of phases happening. I'd be curious if there was any substantial (more than stray) coming back from a different phase on that outbound circuit when the conductor is disconnected from the breaker.
Internet-- It's just diagnostic methodology suggestions unless physically onsite, right?