maybe one of you guys can answer this. I gutted a town house and found 13 romex cables 12/2 in a 2 inch green field changed over to a 2 inch aluminum pipe for lighting to the rooftop. Is this even legal ?
The flex would be causing the cables to be bundled together.
You would have to apply 310.15(B)(2)(a) to the conductors contained in the flex. So 12 AWG conductors, after derating, may only be permitted to be supplied by a 15A breaker.