Re: HV Clearance/OH Lines
Jim
I'm not sure if there is a free web site to access. Perhaps someone else can chime in.
Be sure to read all of the clearance section. It will require you to determine the sag at the highest temperature that the line is designed to operate at. This would be conductor temperature, not ambient temperature. After you determine the sag at the highest temperature, you can compare it to the table to see if you comply. The NESC is very thorough in describing how to determine compliance.
You can imagine that on a cold day, the line would have less, maybe lots less, sag than on a hot day, or a day with the conductors heavily loaded.
If you can tell what type of land this line is traversing, someone can post the clearance listed in the Table.
Jim T