HV J-Box sizing

Status
Not open for further replies.

ch_0124

Member
I am trying to size a J-BOX in which we are gonna splice a 5kv connection to a bus bar and i'm wanting to make sure that we get the backplate far enough off the bus bar and the lugs off the cover of the box. The nec has information on 600v and below but does it say anything about how far the metal cover would have to be off the lug if 5kv. Rule of thumb is one inch for every thousand right. These connections will be taped as well.
 
gonna splice a 5kv connection to a bus bar and i'm wanting to make sure that we get the backplate far enough off the bus bar and the lugs off the cover of the box.


Why the busbar? You must mean you have 3 or more cables.......if only 2, forget the busbar.
 
hv splice box

hv splice box

the box is actually the like the midway point for a pull we're doing. the pull is engineered to be pulled almost 2000 feet from a new power plant to an existing plant and the box is gonna allow us to pull both directions and simplify the pull a lot. i just was wandering if the code book had a table or anything showing clearances from 5kv to a metal cover
 
Why not use a prefabricated junction box? We use a 3' X 5' pullbox with a heavy fiber lid and an open bottom for the minimum size for making primary splices. Be sure to locate your junction box in a pedestrian only area and specify a skid resistant surface. :smile:
 