A Alwayslearningelec Senior Member Location NJ Occupation Estimator Yesterday at 10:00 AM #1 Is this an error? Can the wire insulation be 600v for 15kv?
ron Senior Member Location New York, 40.7514,-73.9925 Yesterday at 10:06 AM #2 The EGC or grounded conductor would be 600V XHHW. The phase conductors would be 15kV rated.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Yesterday at 1:15 PM #3 It is a grounded conductor, so why would it need insulation for high voltage? 250.184(A)(1) in the 2017 code says the minimum insulation level for neutral conductors of solidly grounded systems shall be 600 volts.
It is a grounded conductor, so why would it need insulation for high voltage? 250.184(A)(1) in the 2017 code says the minimum insulation level for neutral conductors of solidly grounded systems shall be 600 volts.