We just recently installed a 7200/12470V Pad mount XFMR, which steps down to 277/480V. We installed 3- 3/4 inch grounds rod (coupled together) within the XFMR pad, to a depth of about 22-23 ft, and that is our XFMR ground. That sounds like overkill, but hard to get a good ground reading in North Florida. Anyway....We are installing a 600 Amp service which ultimately feeds a sandblast booth among other things. The main question I have is, one of our engineers states that we need to pull in a ground from the XFMR into the new 600A service. He also said if we did this, we would not need to put in more ground rods for the service. We (us actually doing the work) are planning to install at least 2 ground rods, either coupled or paralleled, plus bond to a nearby facility beam for the new service. We cannot figure out any logical reason why they want us to pull in a ground with the secondary coming from the XFMR. We are pulling parallel runs of 500kcmil, and they want us to pull parallel 1/0 grounds. The conduit feeding the new service is Schedule 80 PVC. Is this right? wrong? Overkill? Any guidance would be great. Thanks!