Why do some manufacturers of HVAC equipment ground one wire of the secondary on the 24 volt transformer while some leave both wires ungrounded?
Why do some manufacturers of HVAC equipment ground one wire of the secondary on the 24 volt transformer while some leave both wires ungrounded?
The one I saw with a grounded secondary was a 240 volt Trane air handler.I've not noticed. Are the ones you mention 240 volt primary ? If so, ans this is simply a "stab in the dark", but, since there are RARE situations listed in 250.20(A) where they would be required to have a grounded secondary and there is little if any reason not to, by grounding them all the required ones are avaialble.
I agree that it's a manufacturers design choice. If one side of the secondary is grounded, only the other side needs fused. If both sides of the secondary are ungrounded, I believe both sides of the secondary need fused.
Therefore, I believe most manufacturers probably ground one side to eliminate one fuseholder and fuse.