Hi,
Which is more accurate in calculating the actual maximum power draw of the HVAC? 208V

1.) MCA x 208 = 22.8 x 208 = 4.7kW
or
2.) (RLA + FLA) x 208 = (16.7 + 1.7) x 208 = 3.8kW

Thank you


1687975516797.png
 
The current draw shown is just current. You would need to know the power factor to actually calculate the load in Watts.

You can calculate the worst case VA, which would be (16.7+1.7)*208*sqr(3).

MCA tells you what minimum size to make the wires bring the power in.
 
The current draw shown is just current. You would need to know the power factor to actually calculate the load in Watts.

You can calculate the worst case VA, which would be (16.7+1.7)*208*sqr(3).

MCA tells you what minimum size to make the wires bring the power in.
OOPS. I missed that it said the incoming power was "2" phase. So leave out the sqrt(3). Incidentally it is not really two phase.

I am curious though about the model that is indicated as having "4" phase power.
 
For what purpose do you need the 'actual maximum power draw'?

If you are trying to size something like backup system energy storage, then you need both the power consumption during worst case thermal conditions but averaged over a period of time. But if you are trying to size something like the inverter or alternator for that backup system, you need to look at the starting transient. For things like sizing feeder conductors, you need VA not power.

-Jon
 
  • Like
Reactions: Zyb
OOPS. I missed that it said the incoming power was "2" phase. So leave out the sqrt(3). Incidentally it is not really two phase.

I am curious though about the model that is indicated as having "4" phase power.
Thank you. This helps
 
Which is more accurate in calculating the actual maximum power draw of the HVAC? 208V

1.) MCA x 208 = 22.8 x 208 = 4.7kW
or
It's definitely not this one. The MCA has a factor of 125% in it so that would not provide any useful information regarding the maximum power.
 
I really don't get what's up with the 2 phase and 4 phase on the table. I haven't seen any manufacturer making 2 phase equipment in decades, and 4 phase?????????

Was this made up in China with the use of a poor translator?
 
I really don't get what's up with the 2 phase and 4 phase on the table. I haven't seen any manufacturer making 2 phase equipment in decades, and 4 phase?????????

Was this made up in China with the use of a poor translator?

I think it has something to do with the Lunar calendar and the parts of the month when the system will function....
 
Curious about the 2 phase. If your correct then shouldn’t the voltage range for the 1 phase have 120v ? . To me your maybe selecting a unique voltage/phase even though I see the thought process, sometimes you have to assume what the person that prepared the spec sheet is trying to present.
 
Curious about the 2 phase. If your correct then shouldn’t the voltage range for the 1 phase have 120v ? . To me your maybe selecting a unique voltage/phase even though I see the thought process, sometimes you have to assume what the person that prepared the spec sheet is trying to present.

This is two different flavors of 2 phase. Believe me, nobody is installing it on purpose anymore. Where it still exists, when you need replacement stuff, it's all custom made

2p.jpg
 
I
The current draw shown is just current. You would need to know the power factor to actually calculate the load in Watts.

You can calculate the worst case VA, which would be (16.7+1.7)*208*sqr(3).

MCA tells you what minimum size to make the wires bring the power in.
It would be best to look for the mechanical data and compute from there.
Look for the HVAC cooling capacity in BTU per hour and the Energy Efficiency Ratio EER (BTU/watt-hour).
Divide the cooling capacity by the EER and you get the electrical input required in watts.
You need to divide the resulting wattage by the supply voltage and the PF to get the correct amp value.
(BTW, that only tells you of the amp draw of your compressor. You have to add the amp draw of the other auxiliary loads of the HVAC (fans plus control power required.))
 
I

It would be best to look for the mechanical data and compute from there.
Look for the HVAC cooling capacity in BTU per hour and the Energy Efficiency Ratio EER (BTU/watt-hour).
Divide the cooling capacity by the EER and you get the electrical input required in watts.
You need to divide the resulting wattage by the supply voltage and the PF to get the correct amp value.
(BTW, that only tells you of the amp draw of your compressor. You have to add the amp draw of the other auxiliary loads of the HVAC (fans plus control power required.))
Or use 66% of the MCA 😉
 
I really don't get what's up with the 2 phase and 4 phase on the table. I haven't seen any manufacturer making 2 phase equipment in decades, and 4 phase?????????

Was this made up in China with the use of a poor translator?
Had to be…
Probably a misinterpretation of 240/120 3 phase 4 wire, because they would have no frame of reference for anything so out of their experience.
 
Curious about the 2 phase. If you’re correct then shouldn’t the voltage range for the 1 phase have 120v ? . To me your maybe selecting a unique voltage/phase even though I see the thought process, sometimes you have to assume what the person that prepared the spec sheet is trying to present.
Outside of North America, 2-out-of-three phases is called “2 phase”, whereas here we refer to it as “single phase” because for us, true “two phase” power still exists in some pockets (like old Philadelphia).
 
Outside of North America, 2-out-of-three phases is called “2 phase”, whereas here we refer to it as “single phase” because for us, true “two phase” power still exists in some pockets (like old Philadelphia).
Sorry, but what exactly does '2-out-of-three phases' mean here? Do they have equipment that actually draws power from two L-L voltages and not a third, like ours? Or are we just talking about using two out of three available line conductors? I don't see how you get 4-phase from the former convention.

I've always maintained that conductors should be labeled L1, L2, etc and that 'phase" should be used only to refer to a combination of two line conductors. I recognize not everyone is on board with that. But as this example shows the alternatives just really don't make any sense.
 
That chart in the original post is suspect. It isn't using conventional terms in the voltage column. Two hot legs from a three-phase source are NOT two-phase. (See Joe the mechanic above.) And we never did call two-phase "four-phase", even though we could have if we followed the (incorrect) convention that each wire is a "phase".
 