OOPS. I missed that it said the incoming power was "2" phase. So leave out the sqrt(3). Incidentally it is not really two phase.The current draw shown is just current. You would need to know the power factor to actually calculate the load in Watts.
You can calculate the worst case VA, which would be (16.7+1.7)*208*sqr(3).
MCA tells you what minimum size to make the wires bring the power in.
Thank you. This helpsOOPS. I missed that it said the incoming power was "2" phase. So leave out the sqrt(3). Incidentally it is not really two phase.
I am curious though about the model that is indicated as having "4" phase power.
It's definitely not this one. The MCA has a factor of 125% in it so that would not provide any useful information regarding the maximum power.Which is more accurate in calculating the actual maximum power draw of the HVAC? 208V
1.) MCA x 208 = 22.8 x 208 = 4.7kW
or
For conventional single speed compressors, I presume?I have found that HVAC equipment quite reliability draws about 66% of the MCA.
IVe found it is close to that for both mini splits and things like three phase package units.For conventional single speed compressors, I presume?
I really don't get what's up with the 2 phase and 4 phase on the table. I haven't seen any manufacturer making 2 phase equipment in decades, and 4 phase?????????
Was this made up in China with the use of a poor translator?
Curious about the 2 phase. If your correct then shouldn’t the voltage range for the 1 phase have 120v ? . To me your maybe selecting a unique voltage/phase even though I see the thought process, sometimes you have to assume what the person that prepared the spec sheet is trying to present.
It would be best to look for the mechanical data and compute from there.The current draw shown is just current. You would need to know the power factor to actually calculate the load in Watts.
You can calculate the worst case VA, which would be (16.7+1.7)*208*sqr(3).
MCA tells you what minimum size to make the wires bring the power in.
Or use 66% of the MCAI
It would be best to look for the mechanical data and compute from there.
Look for the HVAC cooling capacity in BTU per hour and the Energy Efficiency Ratio EER (BTU/watt-hour).
Divide the cooling capacity by the EER and you get the electrical input required in watts.
You need to divide the resulting wattage by the supply voltage and the PF to get the correct amp value.
(BTW, that only tells you of the amp draw of your compressor. You have to add the amp draw of the other auxiliary loads of the HVAC (fans plus control power required.))
Had to be…I really don't get what's up with the 2 phase and 4 phase on the table. I haven't seen any manufacturer making 2 phase equipment in decades, and 4 phase?????????
Was this made up in China with the use of a poor translator?
Outside of North America, 2-out-of-three phases is called “2 phase”, whereas here we refer to it as “single phase” because for us, true “two phase” power still exists in some pockets (like old Philadelphia).Curious about the 2 phase. If you’re correct then shouldn’t the voltage range for the 1 phase have 120v ? . To me your maybe selecting a unique voltage/phase even though I see the thought process, sometimes you have to assume what the person that prepared the spec sheet is trying to present.
Sorry, but what exactly does '2-out-of-three phases' mean here? Do they have equipment that actually draws power from two L-L voltages and not a third, like ours? Or are we just talking about using two out of three available line conductors? I don't see how you get 4-phase from the former convention.Outside of North America, 2-out-of-three phases is called “2 phase”, whereas here we refer to it as “single phase” because for us, true “two phase” power still exists in some pockets (like old Philadelphia).