T Tdubya90 Member Location Denver Occupation Master electrician Mar 16, 2025 #1 Hello, is anyone aware of any codes preventing strapping the conduit on the same roof blocks as the hvac line set? Thanks
Hello, is anyone aware of any codes preventing strapping the conduit on the same roof blocks as the hvac line set? Thanks
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Mar 16, 2025 #2 No more than using the same building structure element to support pipes or raceways for more than one system.
No more than using the same building structure element to support pipes or raceways for more than one system.
T Tdubya90 Member Location Denver Occupation Master electrician Mar 16, 2025 #3 Sure, but roof blocks aren't really a building structure, it would be more like installing on the same rack...
Sure, but roof blocks aren't really a building structure, it would be more like installing on the same rack...
R rc/retired Senior Member Location Bellvue, Colorado Occupation Master Electrician/Inspector retired Mar 16, 2025 #4 It's still OK. There is no code that prohibits the installation. Ron
J jaggedben Senior Member Location Northern California Occupation Solar and Energy Storage Installer Mar 16, 2025 #5 As long as the line set and conduit are each supported directly by the roof blocks and not supporting each other in any way, then it's absolutely fine.
As long as the line set and conduit are each supported directly by the roof blocks and not supporting each other in any way, then it's absolutely fine.
T Tdubya90 Member Location Denver Occupation Master electrician Mar 19, 2025 #6 Thanks everyone for clearing that up.