I have a project with 4 dual pack HVAC units on the roof of an office.
The nameplate on the unit states: 28.9 FLA and 35 MOCP.
They are feed from a 40 amp 3 pole circuit breaker at the panel.
The fused disconnect on the roof has 35 amp fuses. (120/208)
Inspector says the circuit breakers must be 35 amp.
Can someone point me in the right direction per the NEC 2005 that would dispute the inspector.
Or is the inspector correct?