I am in a disagreement with an plan reviewer on how to properly calculate a load for an HVAC ( commercial) in doing a service or feeder calculation. the HVAC in question is a wall mount unit 3 ton with 10kw heat strip, no dehumidification. 208V 3 phase.

Assumptions
1. Calculate the higher of the two- heat (10KW) or compressor AC loads and use the larger of the two.
2. Use 220.51 for the fixed heat strip at 100%
3. If compressor load is larger follow 220.50 which will take you to 440.6 , AHJ is saying you have to use 1.25% on compressor plus total of fan motors., if you go strictly by 440.6 I do not see any indication that you use 1.25
4. AHJ is also saying heat load is continuous and should be at 1.25%

thanks,
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I am in a disagreement with an plan reviewer on how to properly calculate a load for an HVAC ( commercial) in doing a service or feeder calculation. the HVAC in question is a wall mount unit 3 ton with 10kw heat strip, no dehumidification. 208V 3 phase.

Assumptions
1. Calculate the higher of the two- heat (10KW) or compressor AC loads and use the larger of the two.
2. Use 220.51 for the fixed heat strip at 100%
3. If compressor load is larger follow 220.50 which will take you to 440.6 , AHJ is saying you have to use 1.25% on compressor plus total of fan motors., if you go strictly by 440.6 I do not see any indication that you use 1.25
4. AHJ is also saying heat load is continuous and should be at 1.25%

thanks,

See 440.33 rather than 440.6 for the A/C load.

I think the AHJ is wrong about the heat...424.3(B) says that fixed electric space heating shall be considered continuous load for branch circuit sizing. It says nothing about feeder/service sizing.
 