electro7
Senior Member
- Location
- Northern CA, US
- Occupation
- Electrician, Solar and Electrical Contractor
We are doing a project changing multiple rooftop HVAC units out but installing new disconnects, fuses, and utilizing the existing wiring. We are having to extend the wiring in most cases. There are some existing breakers that are larger than the fuses we are using for the new units. As an example, there may be a unit with existing #8 originating from a 50A breaker that we are replacing with a unit that requires a max fuse of 30A. From the load side of these disconnects, we are wired in with #10, but when we splice and extend the existing conductors, can we use #10?
Is the HVAC circuit considered a feeder since it lands at a fused disconnect? If so, I would assume we could change to #10 as long as we follow the feeder tap rules in 240. If it's not considered a feeder, then I would assume we would need to keep #8 to the line side of the disconnect.
Thanks again!