Hi guys,
Sorry to bore you guys with this topic again but I'm having issues with an HVAC company that is installing a new system in my Mother's house. She is a 90 yr old widow (Dad passed away 15 yrs ago) and I just recently retired from the Navy after 30yrs and I am now dedicated to making her home safe and sound for her remaining yrs.
Here are some details:
Distance from main breaker panel (MBP) (in basement) to outside corner of house (adjacent to and right above MBP: 48"
This corner is where the A/C Compressor unit disconnect (they have provided a 60amp non-fused disconnect box) will be. The corner mounted disconnect will be in a direct line of sight from the compressor.
Distance from corner disconnect to compressor: 25'
The manufacturer's (Goodman) label plate says "Max. Fuse Amps or Max. Circuit Breaker 40" and
"Min. Circuit Amps 23.9" and "A.C. Volts 208 - 230"
The problem I'm having is that the installer is trying to install the 60amp disconnect, 8 awg whip, and 60 amp breaker. I've told them that all of that is oversized and that based upon the 2014 NEC, they should be using a 40 amp breaker, 10 awg wire and 40 amp disconnect.
I have researched everything I can find (NEC, local codes, Mike Holt forums and etc.) and cannot find out why they are so insistent on their plan. The installers are falling back on the old "That's what the boss told us to use."
Any help would be appreciated and I'll show them your all's comments - unless I'm wrong in which I will tuck my tail between my legs and walk away.
Thanks,
Dave
Sorry to bore you guys with this topic again but I'm having issues with an HVAC company that is installing a new system in my Mother's house. She is a 90 yr old widow (Dad passed away 15 yrs ago) and I just recently retired from the Navy after 30yrs and I am now dedicated to making her home safe and sound for her remaining yrs.
Here are some details:
Distance from main breaker panel (MBP) (in basement) to outside corner of house (adjacent to and right above MBP: 48"
This corner is where the A/C Compressor unit disconnect (they have provided a 60amp non-fused disconnect box) will be. The corner mounted disconnect will be in a direct line of sight from the compressor.
Distance from corner disconnect to compressor: 25'
The manufacturer's (Goodman) label plate says "Max. Fuse Amps or Max. Circuit Breaker 40" and
"Min. Circuit Amps 23.9" and "A.C. Volts 208 - 230"
The problem I'm having is that the installer is trying to install the 60amp disconnect, 8 awg whip, and 60 amp breaker. I've told them that all of that is oversized and that based upon the 2014 NEC, they should be using a 40 amp breaker, 10 awg wire and 40 amp disconnect.
I have researched everything I can find (NEC, local codes, Mike Holt forums and etc.) and cannot find out why they are so insistent on their plan. The installers are falling back on the old "That's what the boss told us to use."
Any help would be appreciated and I'll show them your all's comments - unless I'm wrong in which I will tuck my tail between my legs and walk away.
Thanks,
Dave