qcroanoke
Sometimes I don't know if I'm the boxer or the bag
- Location
- Roanoke, VA.
- Occupation
- Sorta retired........
Have a HVAC redundant controller with a installation manual that states, " A reliable earth ground must be connected in addition to any grounding from conduit."
If I use the HVAC unit's equipment ground for this do I have to pull the same size ground that the unit has to the controller or can I downsize it to #12? Any unit we wire is usually a #10 ground.
The controller is all 24 v.a.c. No line voltage is present.
Also, If we run a conduit from a nearby receptacle to the controller and pull only a ground wire through
it are we creating a potential problem? I have heard it's something that you don't want to do.
Thanks!
If I use the HVAC unit's equipment ground for this do I have to pull the same size ground that the unit has to the controller or can I downsize it to #12? Any unit we wire is usually a #10 ground.
The controller is all 24 v.a.c. No line voltage is present.
Also, If we run a conduit from a nearby receptacle to the controller and pull only a ground wire through
it are we creating a potential problem? I have heard it's something that you don't want to do.
Thanks!