hey all-
this sounds silly as i type it, but here goes.
at a hvac compressor disco, the name plate rating has a "minimum circuit ampacity" of 26A, and a "maximum fuse size" of 40A.
i understand that the wire size can be based on the min circuit amps. (don't want to start that argument!)
my question is about the maximum fuse size-
does the fuse size need to be 40A? could it be 35A? why not 30A?
i have always "called" it as "maximum overcurrent protection required at condenser" (per manufacturers instructions?)
is there anywhere (code/install instructions/etc?) that actually REQUIRES a 40A fuse, if the nameplate rating is "maximum 40A"???
thanks!