I checked out a hvac unit today in an apartment in a large apartment building to see why a recently installed unit was tripping the breaker. That answer was simple. It was connected to a 2 pole 30. MCA for it is 47. So the branch circuit needs to be upgraded to a 50 amp circuit. Obviously an electrician did not wire it. Someone just connected a new unit to the existing circuit.
My question is about the disconnect. There wasn't one within site of the unit. All there is is a circuit breaker for it in a different room. There was no sign of a means to lock the breaker in the off position. Doesn't the unit need a disconnect within site?
My question is about the disconnect. There wasn't one within site of the unit. All there is is a circuit breaker for it in a different room. There was no sign of a means to lock the breaker in the off position. Doesn't the unit need a disconnect within site?