Therealcrt
Senior Member
- Location
- Kansas City
- Occupation
- Electrician
I’m soon gonna be wiring a make up air unit ( HEAT ONLY) and the heat source is Gas. the nameplate provides the following ; 480v 3PH the MCA 27.1 and MOP is 45. I planned on using power from an existing make up air unit that will be demoed. And I traced it back to the panel and it’s 10 gauge wire on a 30 amp QMB branch switch fused so my question is on the new unit obviously I’m sizing the wire according to 27.1 A which I’m safe to use 10 gauge wire, but I’m curious if I can use that existing 30 amp QMB branch switch? I know I can’t go over 45 A but can I safely run it at 30 A otherwise I’d have to switch out the whole bucket to a 60 amp branch switch infuse it to 45.