HVAC Engineering question for Bathroom Exhaust

Merry Christmas

Michael1985

Member
Location
toronto
Occupation
Builder - Licensed HVAC Technician
Hi everyone. hoping to get some input regarding my bathroom exhaust fan Panasonic 90CFM. I live in a condo and currently renovating the bathroom. The existing 5" duct runs vertical from the fan to the outside 35 feet with (2) 90 degree elbows. I will attempt to reposition the fan to remove (1) 90 degree elbow. That said, my question is.

1. Do I require a booster for a bathroom exhaust fan that has a 35 foot run? Seeing that the condo developer never installed one, I assume it was not required to code.
FYI, the Dryer fan has a booster and it also is 35 feet run.

2. I would like to reduce the 5" duct down to 4" duct upon entering the bathroom to the actual fan outlet. The existing 5" duct from outside will remain until it reaches the bathroom at which point I would like to reduce it to 4". Will there be a significant impact loss by reducing at the fan?

Greatly appreciate any input.

Thanks,

M
 

Michael1985

Member
Location
toronto
Occupation
Builder - Licensed HVAC Technician
Thanks for your input, that's a great suggestion. In my line of work, it's not a requirement as per code in the province of Ontario but I have installed them in the past on certain projects that had multiple 90 degree elbows in the path. That said, this situation is mainly a straight vertical path so a larger fan will also do the trick.
Thanks.
 
Thanks for your input, that's a great suggestion. In my line of work, it's not a requirement as per code in the province of Ontario but I have installed them in the past on certain projects that had multiple 90 degree elbows in the path. That said, this situation is mainly a straight vertical path so a larger fan will also do the trick.
Thanks.
I'm sure there is a scientific way to calculate the flow reduction from the ducting, but the amount of flow actually required for the bathroom is probably not really an exact science and I prefer more flow anyway. 💩
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
2. I would like to reduce the 5" duct down to 4" duct upon entering the bathroom to the actual fan outlet. The existing 5" duct from outside will remain until it reaches the bathroom at which point I would like to reduce it to 4". Will there be a significant impact loss by reducing at the fan?
I the fan outlet is 4", you're good; if it's 5", then no.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
You can use a duct pressure loss calculator, such as this one:


For 100 CFM through a smooth (rigid, not flex) 5" duct, the pressure loss will be 0.213" wc per 100ft; for 4" duct, it will be be 0.654" w.c. per 100 ft. So each foot of 4" duct would be equivalent to 3.07 feet of 5" duct in terms of the pressure loss.

You can check your fan installation manual; it should have information on either the maximum allowable pressure drop for proper operation (I'm thinking around 0.1" wc) or the maximum allowable length. You also need to know the equivalent length to use for each elbow; IMC Table 504.9.4.1 says to use 5' for a mitered 4" 90" elbow on a clothes dryer exhaust; that seems like a reasonable starting point, or the fan manual may specify. A 4" to 5" transition will also have an equivalent length, but if it's somewhat tapered, that shouldn't be more than a foot or two, I would think.

Cheers, Wayne
 

Michael1985

Member
Location
toronto
Occupation
Builder - Licensed HVAC Technician
You can use a duct pressure loss calculator, such as this one:


For 100 CFM through a smooth (rigid, not flex) 5" duct, the pressure loss will be 0.213" wc per 100ft; for 4" duct, it will be be 0.654" w.c. per 100 ft. So each foot of 4" duct would be equivalent to 3.07 feet of 5" duct in terms of the pressure loss.

You can check your fan installation manual; it should have information on either the maximum allowable pressure drop for proper operation (I'm thinking around 0.1" wc) or the maximum allowable length. You also need to know the equivalent length to use for each elbow; IMC Table 504.9.4.1 says to use 5' for a mitered 4" 90" elbow on a clothes dryer exhaust; that seems like a reasonable starting point, or the fan manual may specify. A 4" to 5" transition will also have an equivalent length, but if it's somewhat tapered, that shouldn't be more than a foot or two, I would think.

Cheers, Wayne
Thanks for the suggestion Wayne. I will certainly use the loss calculator to determine the pressure loss. 🙏
 