I'm trying to run through the appropriate load calculations for my home. This is for two reasons: 1.) To get a baseline as I'm remodelling 2.) To run through a real-world scenario as I prepare for my exam.
Since this is my first real-world calculation, it's been a bit slow. The most confusing seems to be the HVAC unit. I have a gas furnace with electric A/C. The nameplate states the following:
Compressors: 12.1 RLA, 57 LRA
Indoor Blower: 1.7 FLA, 1/5 hp
Outdoor Blower: 1.0 FLA, 1/6 hp
Combustion Blower: 0.67 FLA, 1.30 hp
Min Ckt Ampacity: 17.9 A
Max Fuse Size: 25 A
Does this sound right for the HVAC Branch Circuit Load and its contribution to the Feeder/Service Calculation?
12.1 * 1.25 + 1.7 + 1.0 + 0.67 = 18.5 A
And as a newbie to load calculations, is there anything else I should be considering that I would most likely miss?
Thank you in advance for your assistance.