It would be a panel only for the 12 condenser units in a residential buildingIf you are running a sub panel for just those units I believe you will need to use a 300 amp overcurrent protective device
Not sure what you mean by what type of sub panel
Sorry the main building is 3 phaseSingle phase
the main building is 3 phasesingle phase or 3 phase supply ?
I get:
12 units supplied L-L, 4 on each of the 3 pairs of the 3 phase supply. First unit at MCA = 25A. Second through fourth units at nameplate rating, 20.5A. Total is 25 + 20.5*3 = 86.5A on each of the 3 pairs. Load on each line conductor is sqrt(3) * 86.5A = 150A.
Cheers, Wayne
If I decided to use a single phase sub panel what would I need?I get:
12 units supplied L-L, 4 on each of the 3 pairs of the 3 phase supply. First unit at MCA = 25A. Second through fourth units at nameplate rating, 20.5A. Total is 25 + 20.5*3 = 86.5A on each of the 3 pairs. Load on each line conductor is sqrt(3) * 86.5A = 150A.
Cheers, Wayne
You’d need to provide a 300 amp ocpd to protect a single phase sub panel feeding those 12 units. 12 units- MCA 25 amps - 300 amp ocpdIf I decided to use a single phase sub panel what would I need?
That's more than is required--MCA includes a 125% factor for the largest motor (or equivalent when you have power conversion equipment, I assume), and the feeder only requires the 125% factor once, not 12 times.You’d need to provide a 300 amp ocpd to protect a single phase sub panel feeding those 12 units. 12 units- MCA 25 amps - 300 amp ocpd
That's more than is required--MCA includes a 125% factor for the largest motor (or equivalent when you have power conversion equipment, I assume), and the feeder only requires the 125% factor once, not 12 times.
So 25+11*20.5 = 250.5, I'd say a 250A supply would suffice. [Yes, I'm dropping the 0.5.]
Cheers, Wayne
Eu entendo:
12 unidades fornecidas LL, 4 em cada um dos 3 pares do fornecimento trifásico. Primeira unidade em MCA = 25A. Segunda a quarta unidades na classificação da placa de identificação, 20,5A. O total é 25 + 20,5*3 = 86,5A em cada um dos 3 pares. A carga em cada condutor de linha é sqrt(3) * 86,5A = 150A.
Saudações, Wayne
Eu entendo:
12 unidades fornecidas LL, 4 em cada um dos 3 pares do fornecimento trifásico. Primeira unidade em MCA = 25A. Segunda a quarta unidades na classificação da placa de identificação, 20,5A. O total é 25 + 20,5*3 = 86,5A em cada um dos 3 pares. A carga em cada condutor de linha é sqrt(3) * 86,5A = 150A.
Saudações, Wayne
Thank you for your help!I get:
12 units supplied L-L, 4 on each of the 3 pairs of the 3 phase supply. First unit at MCA = 25A. Second through fourth units at nameplate rating, 20.5A. Total is 25 + 20.5*3 = 86.5A on each of the 3 pairs. Load on each line conductor is sqrt(3) * 86.5A = 150A.
Cheers, Wayne
I appreciate your help!That's more than is required--MCA includes a 125% factor for the largest motor (or equivalent when you have power conversion equipment, I assume), and the feeder only requires the 125% factor once, not 12 times.
So 25+11*20.5 = 250.5, I'd say a 250A supply would suffice. [Yes, I'm dropping the 0.5.]
Cheers, Wayne
Can you help me with this other question: if I decide to place this panel near the condensers, would it still be necessary to install the disconnect for each machine too?I get:
12 units supplied L-L, 4 on each of the 3 pairs of the 3 phase supply. First unit at MCA = 25A. Second through fourth units at nameplate rating, 20.5A. Total is 25 + 20.5*3 = 86.5A on each of the 3 pairs. Load on each line conductor is sqrt(3) * 86.5A = 150A.
Cheers, Wayne
Can you help me with this other question: if I decide to place this panel near the condensers, would it still be necessary to install the disconnect for each machine too?
I don't see how you got there based on 430.62 which is for overcurrent protective device size. I know 430 is for motor but I thought 440 sent us to 430That's more than is required--MCA includes a 125% factor for the largest motor (or equivalent when you have power conversion equipment, I assume), and the feeder only requires the 125% factor once, not 12 times.
So 25+11*20.5 = 250.5, I'd say a 250A supply would suffice. [Yes, I'm dropping the 0.5.]
Cheers, Wayne
I was calculating the feeder "MCA". You're correct that the feeder MOCPD would be higher.I understand that you take one motor and take the 20.5 x 250% for one motor plus the sum of the 11 others. Isn't that what it states?
Yep, I did round up and forgot that I shouldn't. That's one of the few places (I think) in the NEC where you don't round upI was calculating the feeder "MCA". You're correct that the feeder MOCPD would be higher.
430.62 says to take the MOCPD for the largest motor and add the FLCs for the other motors. The nameplate says the MOCPD is 40A, so the calculation would be 40 + 11*20.5 = 265.5. I don't see any provision for rounding up, so the largest standard size is 250A.
I didn't double check all the sections of 430 for this post or the previous one, so I may have overlooked something.
Cheers, Wayne
I understand thank you for the help.Read 440.14 for the rules for ac disconnects . If the panel is within sight of all the units , and that means visible from every unit and within 50’ of every unit , then the breaker would be allowed to be the sole disconnecting means for each unit.
In my mind it’s more practical to have disconnects near the units or on the unit if possible simply because unless it’s a really short run i assume you’ll be transitioning from solid conduit to LFMC somewhere before the unit anyways
Sent from my iPhone using Tapatalk
I made the same mistake and rounded the ocpd up to 300 amps but 430.62 doesn’t allow it to exceed 265.5 amps here so it would be a 250 amp ocpd .Yep, I did round up and forgot that I shouldn't. That's one of the few places (I think) in the NEC where you don't round up