Hey guys, I have a job with 12 condensers with this information. Doubting myself on the type of subpanel to support this. Any tips and suggestions
 

Attachments

  • IMG_3285.jpeg
    IMG_3285.jpeg
    1.9 MB · Views: 33
If you are running a sub panel for just those units I believe you will need to use a 300 amp overcurrent protective device

Not sure what you mean by what type of sub panel
 
I get:

12 units supplied L-L, 4 on each of the 3 pairs of the 3 phase supply. First unit at MCA = 25A. Second through fourth units at nameplate rating, 20.5A. Total is 25 + 20.5*3 = 86.5A on each of the 3 pairs. Load on each line conductor is sqrt(3) * 86.5A = 150A.

Cheers, Wayne
 
I get:

12 units supplied L-L, 4 on each of the 3 pairs of the 3 phase supply. First unit at MCA = 25A. Second through fourth units at nameplate rating, 20.5A. Total is 25 + 20.5*3 = 86.5A on each of the 3 pairs. Load on each line conductor is sqrt(3) * 86.5A = 150A.

Cheers, Wayne

I get:

12 units supplied L-L, 4 on each of the 3 pairs of the 3 phase supply. First unit at MCA = 25A. Second through fourth units at nameplate rating, 20.5A. Total is 25 + 20.5*3 = 86.5A on each of the 3 pairs. Load on each line conductor is sqrt(3) * 86.5A = 150A.

Cheers, Wayne
If I decided to use a single phase sub panel what would I need?
 
You’d need to provide a 300 amp ocpd to protect a single phase sub panel feeding those 12 units. 12 units- MCA 25 amps - 300 amp ocpd
That's more than is required--MCA includes a 125% factor for the largest motor (or equivalent when you have power conversion equipment, I assume), and the feeder only requires the 125% factor once, not 12 times.

So 25+11*20.5 = 250.5, I'd say a 250A supply would suffice. [Yes, I'm dropping the 0.5.]

Cheers, Wayne
 
That's more than is required--MCA includes a 125% factor for the largest motor (or equivalent when you have power conversion equipment, I assume), and the feeder only requires the 125% factor once, not 12 times.

So 25+11*20.5 = 250.5, I'd say a 250A supply would suffice. [Yes, I'm dropping the 0.5.]

Cheers, Wayne

You’re 100% correct . I had a stupid moment and you caught it and I appreciate that lol. We can size this feeder in accordance with 430.24 . So like you said the load for these 12 units is calculated at 250.5 amps .
And like you said a 250 amp supply would definitely suffice but a 300 amp ocpd would be compliant for this 250.5 amp load if need be because of that .5 amps lol


Sent from my iPhone using Tapatalk
 
Eu entendo:

12 unidades fornecidas LL, 4 em cada um dos 3 pares do fornecimento trifásico. Primeira unidade em MCA = 25A. Segunda a quarta unidades na classificação da placa de identificação, 20,5A. O total é 25 + 20,5*3 = 86,5A em cada um dos 3 pares. A carga em cada condutor de linha é sqrt(3) * 86,5A = 150A.

Saudações, Wayne

Eu entendo:

12 unidades fornecidas LL, 4 em cada um dos 3 pares do fornecimento trifásico. Primeira unidade em MCA = 25A. Segunda a quarta unidades na classificação da placa de identificação, 20,5A. O total é 25 + 20,5*3 = 86,5A em cada um dos 3 pares. A carga em cada condutor de linha é sqrt(3) * 86,5A = 150A.

Saudações, Wayne

I get:

12 units supplied L-L, 4 on each of the 3 pairs of the 3 phase supply. First unit at MCA = 25A. Second through fourth units at nameplate rating, 20.5A. Total is 25 + 20.5*3 = 86.5A on each of the 3 pairs. Load on each line conductor is sqrt(3) * 86.5A = 150A.

Cheers, Wayne
Thank you for your help!
 
That's more than is required--MCA includes a 125% factor for the largest motor (or equivalent when you have power conversion equipment, I assume), and the feeder only requires the 125% factor once, not 12 times.

So 25+11*20.5 = 250.5, I'd say a 250A supply would suffice. [Yes, I'm dropping the 0.5.]

Cheers, Wayne
I appreciate your help!
 
I get:

12 units supplied L-L, 4 on each of the 3 pairs of the 3 phase supply. First unit at MCA = 25A. Second through fourth units at nameplate rating, 20.5A. Total is 25 + 20.5*3 = 86.5A on each of the 3 pairs. Load on each line conductor is sqrt(3) * 86.5A = 150A.

Cheers, Wayne
Can you help me with this other question: if I decide to place this panel near the condensers, would it still be necessary to install the disconnect for each machine too?
 
Can you help me with this other question: if I decide to place this panel near the condensers, would it still be necessary to install the disconnect for each machine too?

Read 440.14 for the rules for ac disconnects . If the panel is within sight of all the units , and that means visible from every unit and within 50’ of every unit , then the breaker would be allowed to be the sole disconnecting means for each unit.
In my mind it’s more practical to have disconnects near the units or on the unit if possible simply because unless it’s a really short run i assume you’ll be transitioning from solid conduit to LFMC somewhere before the unit anyways


Sent from my iPhone using Tapatalk
 
That's more than is required--MCA includes a 125% factor for the largest motor (or equivalent when you have power conversion equipment, I assume), and the feeder only requires the 125% factor once, not 12 times.

So 25+11*20.5 = 250.5, I'd say a 250A supply would suffice. [Yes, I'm dropping the 0.5.]

Cheers, Wayne
I don't see how you got there based on 430.62 which is for overcurrent protective device size. I know 430 is for motor but I thought 440 sent us to 430

I understand that you take one motor and take the 20.5 x 250% for one motor plus the sum of the 11 others. Isn't that what it states?
 
Last edited:
I understand that you take one motor and take the 20.5 x 250% for one motor plus the sum of the 11 others. Isn't that what it states?
I was calculating the feeder "MCA". You're correct that the feeder MOCPD would be higher.

430.62 says to take the MOCPD for the largest motor and add the FLCs for the other motors. The nameplate says the MOCPD is 40A, so the calculation would be 40 + 11*20.5 = 265.5. I don't see any provision for rounding up, so the largest standard size is 250A.

I didn't double check all the sections of 430 for this post or the previous one, so I may have overlooked something.

Cheers, Wayne
 
I was calculating the feeder "MCA". You're correct that the feeder MOCPD would be higher.

430.62 says to take the MOCPD for the largest motor and add the FLCs for the other motors. The nameplate says the MOCPD is 40A, so the calculation would be 40 + 11*20.5 = 265.5. I don't see any provision for rounding up, so the largest standard size is 250A.

I didn't double check all the sections of 430 for this post or the previous one, so I may have overlooked something.

Cheers, Wayne
Yep, I did round up and forgot that I shouldn't. That's one of the few places (I think) in the NEC where you don't round up
 
Read 440.14 for the rules for ac disconnects . If the panel is within sight of all the units , and that means visible from every unit and within 50’ of every unit , then the breaker would be allowed to be the sole disconnecting means for each unit.
In my mind it’s more practical to have disconnects near the units or on the unit if possible simply because unless it’s a really short run i assume you’ll be transitioning from solid conduit to LFMC somewhere before the unit anyways


Sent from my iPhone using Tapatalk
I understand thank you for the help.
 