Larry, thanks for the input. At this time, my customer is undecided on a unit. I will use the 2kva per ton rule of thumb as worst case. Once we determine the unit, I will get nameplate data. When looking at nameplate data, what is used to determine the kva rating? I would assume V x I x 1.73 for 3-phase or V x I for 1-phase. Is this the correct approach?
Thanks again.
Steve
Check out 440.4(B), "Multimotor and combination-load equipment shall be provided with a visible nameplate marked with the maker's name, the rating in volts, frequency and number of phases,
minimum supply circuit conductor ampacity, the maximum rating of the branch-circuit short-circuit and ground-fault protective device [breaker]..."
If the lable isn't there the unit may not be listed.
Check out the following:
Unit Multiplied by Converted Unit
refrigerative ton 3,516.852 842 watt
refrigerative ton 3.516 852 842 kilowatt
refrigerative ton 4.714 279 949 horsepower
refrigerative ton 12,000 BTU/h
Also:
Unit Multiplied by Converted Unit
kilowatt 1000 watt
kilowatt 1.340 482 57 horsepower
kilowatt 0.284 345 14 refrigerative ton
kilowatt 3412.142 45 BTU/h