HVAC Load calculator

Status
Not open for further replies.

mike30jr

New member
Location
thomasville, GA
I am currently bidding a job that requires feeding thirty seven mini split ac units out of two panels. I was looking for the load calculator for hvac equipment, and found that it usually calls for you to figure hvac equipment at 100%. I was just woundering if this is the case for a total hvac fed panel. This seems to be a huge load, and wanted to make sure that this is right?
 

kwired

Electron manager
Location
NE Nebraska
When the temperature is highest or lowest (or beyond) the temperature the systems were designed for they will be 100% loaded, and the users would sure appreciate that they continue to run at those times.
 
Status
Not open for further replies.