mkgrady
Senior Member
- Location
- Massachusetts
When trying to determine the adequacy of a service for a single family residence and all you know about the HVAC equipment (Mini-split system) is the minimum circuit ampacity, how is this info used to verify the service size? I realize the load in watts is counted at 100% in the calculation but all I have is the MCA. I'm troubled by the outcome of the calculation because when I take an amperage reading of something that has a MCA of say 22 amps it never seems to come close to that much.
For example if I am looking at an existing service that has a calculated load of 80 amps in accordance with 220 and the MCA of the added HVAC is 22 amps (240V) then the added load seems to put it over 100 by 2 amps. Is there another way to calculate it? Obviously I am trying to keep the number under 100.
For example if I am looking at an existing service that has a calculated load of 80 amps in accordance with 220 and the MCA of the added HVAC is 22 amps (240V) then the added load seems to put it over 100 by 2 amps. Is there another way to calculate it? Obviously I am trying to keep the number under 100.