I was installing a Tropical T-55 pool heater. A typical heat pump that has an MCA of 19.7 amps. The wire has to be able to carry the calculated load or the MCA rating. ( In this case 12 gauge/20 amp MC cable) But what about the MOP? The name plate states a maximum fuse size of 30 Amps. Can we wire the heater with 12 gauge MC and load it on a 30 amp breaker and be code compliant. I do believe you still have to think about the load on the breaker. Is there a provision that will let you up the size of the OCPD and still let you use the 12 gauge MC for the calculated load. Overload protection should either be built into the motor or at the disconnect. Thanks for your help in trying to clear this issue up for me.