switchleg45
Member
- Location
- Ft Myers,FL
I, as well as many of my colleagues, would like to know: If the nameplate rating on an HVAC air handling unit w/heater kit is "Volts: 240/208, Amps 40.0/34.6"...the fundamental rule that states "as voltage is increased amperage decreases" seems to not fit. Can one of you highly knowledgeable engineers enlighten me? Can you direct me to information sources I can study to help understand this conflict?
Doing load calcs for Seisco tankless water heater install. AHJ says he will not allow the 40% demand per optional calc, only the 75% demand per the standard calc.
Doing load calcs for Seisco tankless water heater install. AHJ says he will not allow the 40% demand per optional calc, only the 75% demand per the standard calc.