I had a customer call and complain that his house seems to eat outside A/C units on a regular basis.
Specifically, the compressors seem to burn out within a couple of years, where they should be lasting 15-20.
The HVAC guys are telling him that the power company must be supplying too little voltage, and that is what is burning them out.
So, I checked the incoming supply and measured 249.5 Volts. While that seems a bit high, it is within tolerance of 5% mandated by the PSC.
However, the nameplate on the unit states the rating is 230 Volts.
So, with an overvoltage of almost 20 Volts, that amounts to 8.5% too much, beyond an ideal 5%.
Would this be a factor, and should I recommend installing a buck transformer to lower the incoming voltage to closer to the nameplate rating?
The unit is a Coleman, self-contained heat/ac outside pak.