Hvac panel size

Status
Not open for further replies.

PowerdT

Senior Member
Location
San Diego
Occupation
Electrical Engineer
I have 150A, 3P panel.
The hvac loads are (3) 40A MCA, MOP 50A

Do you think 150A panel should be enough.

I wanted to verify not to run into nuisances problem because 150A 80% continues is at 120A.

Please advice?
 
The MCA has 25% added to the largest load of the unit (typically the compressor) so 3*40 amps is not the actual current with the units running.
 
I have 150A, 3P panel.
The hvac loads are (3) 40A MCA, MOP 50A

Do you think 150A panel should be enough.

I wanted to verify not to run into nuisances problem because 150A 80% continues is at 120A.

Please advice?
You meet code minimums. Is there some possibility of nuisance tripping? Possibly, but it seems unlikely.
 
The panel is only feeding this 3 loads.

Hopefully they should not turn all them on at the same time either for the inrush
After power outage is when that is most likely, but if that is a problem staggered time delays can resolve this.

If they are soft started/VFD driven probably isn't a problem anyway.
 