ThanksYou are good, both from a practical standpoint and an NEC standpoint. I find actual HVAC draw is about 2/3 of the MCA
You meet code minimums. Is there some possibility of nuisance tripping? Possibly, but it seems unlikely.I have 150A, 3P panel.
The hvac loads are (3) 40A MCA, MOP 50A
Do you think 150A panel should be enough.
I wanted to verify not to run into nuisances problem because 150A 80% continues is at 120A.
Please advice?
The panel is only feeding this 3 loads.You meet code minimums. Is there some possibility of nuisance tripping? Possibly, but it seems unlikely.
After power outage is when that is most likely, but if that is a problem staggered time delays can resolve this.The panel is only feeding this 3 loads.
Hopefully they should not turn all them on at the same time either for the inrush