blueheels2
Senior Member
- Location
- Raleigh, NC
- Occupation
- Electrical contractor
I have an inside AHU with auxiliary heat strips. Nameplate is:
Minimum circuit ampacity:58.3 amp
MOCP: 60 amp
This is a changeout.
Old unit was fed with 6-2 nm-b. Ampacity of this is 55 but 240.4(B) says it can be protected by a 60 amp breaker. My buddy says his old electrician wired that like this all the time and passed inspection.
I say this is incorrect that the unit needs to be wired in 4-2nm-b or installed in conduit and wired with #6 thhn.
What do you guys say?
Minimum circuit ampacity:58.3 amp
MOCP: 60 amp
This is a changeout.
Old unit was fed with 6-2 nm-b. Ampacity of this is 55 but 240.4(B) says it can be protected by a 60 amp breaker. My buddy says his old electrician wired that like this all the time and passed inspection.
I say this is incorrect that the unit needs to be wired in 4-2nm-b or installed in conduit and wired with #6 thhn.
What do you guys say?