HVAC RTU existing breaker size?

Status
Not open for further replies.

HipHopHead

Member
Location
NJ
Occupation
Electrical contractor
RTU is being fed by 3 pole 70.
Maximum breaker/fuse is 50.
MCA is 41
I used a fused disco w/ 3 - 50 amp fuses
Can someone refresh my brain, to the article that tells me what that breaker should be sized at?

Thanks in advance
 
Take a look at this recent thread:
 
With #4 cu you could use anything up to a 90 amp breaker. Your havc is protected by the disconnect so all you are protecting is the #4 feeder/ branch circuit
 
Thanks for the link. Great conversation. In other words Im not required to do anything to the breaker, due to the fused disconnect providing the OCP, as long as it properly sized for the conductor.
 
Thanks for the link. Great conversation. In other words Im not required to do anything to the breaker, due to the fused disconnect providing the OCP, as long as it properly sized for the conductor.
Yup. The existing 70 amp OCPD is protecting the 90 amp feeder conductors.
 