HVAC Service receptacle and light

Status
Not open for further replies.

daddynuz2

New User
Location
Wall, NJ USA
As it is a requirement to have a Service receptacle and light on a rooftop H.V.A.C. equipment. Is it possible to use a transformer to be tapped from the 240 Volt feeders that would step down voltage to have 120 volt receptacle and light powered from the feeders making the tap ahead of the service disconnect. ( i imagine this could be done with 2 legs of three phase conductors in each case there is no grounded conductor run from the power source.
 

Attachments

  • rooftop hvac.jpg
    rooftop hvac.jpg
    63.2 KB · Views: 1
  • rooftop 5 hvac.jpg
    rooftop 5 hvac.jpg
    13.9 KB · Views: 1
As it is a requirement to have a Service receptacle and light on a rooftop H.V.A.C. equipment. Is it possible to use a transformer to be tapped from the 240 Volt feeders that would step down voltage to have 120 volt receptacle and light powered from the feeders making the tap ahead of the service disconnect. ( i imagine this could be done with 2 legs of three phase conductors in each case there is no grounded conductor run from the power source.

I’m not required to have light, just a receptacle. Yes, you could tap the feeders but you will now need to include the transformer load into the calculation for that feeder. Add CB/fuse protection for the transformer, line and/or load side. GEC?

I have have seen where RTUs have a receptacle included. Handy.
 