So I have a chiller, and like almost all HVAC Equipment, it has a short circuit withstand rating of 5KA.
It has a MCA of about 500 amps, so I'm obviously going to supply it with a system that has a much greater available fault current than 5KA, which is a code violation.
I can add a fused disconnect with current limiting fuses to the units supply. But my understanding is that this doesn't necessarily make everything code compliant. Is that correct? If so, is there any code compliant way to install this short of looping coils of 500KCM wire around the building until the fault current is below 5KA? (My voltage drop along the feeder will probably be much more than 5% by the time I do that, so now it will cause other problems.)
The last time this happened, we just required the manufacturer to provided a higher rated short circuit withstand rating. And after a lot of back and forth, all they did was to add the same fused disconnect I would have added, except they charged a lot more for it.
So what does anyone do in this situation? Its just crazy to have a 5KA rating on something that needs 500 amps or more to run.
It has a MCA of about 500 amps, so I'm obviously going to supply it with a system that has a much greater available fault current than 5KA, which is a code violation.
I can add a fused disconnect with current limiting fuses to the units supply. But my understanding is that this doesn't necessarily make everything code compliant. Is that correct? If so, is there any code compliant way to install this short of looping coils of 500KCM wire around the building until the fault current is below 5KA? (My voltage drop along the feeder will probably be much more than 5% by the time I do that, so now it will cause other problems.)
The last time this happened, we just required the manufacturer to provided a higher rated short circuit withstand rating. And after a lot of back and forth, all they did was to add the same fused disconnect I would have added, except they charged a lot more for it.
So what does anyone do in this situation? Its just crazy to have a 5KA rating on something that needs 500 amps or more to run.