Can anyone please verify if I sized Air Condition correctly. Thank you in advance.
The system is 480V, 3p,60Hz
The system is 480V, 3p,60Hz
MCA is given 22.6A
MOP is given 25A
FLA is given 24
LRA is given 130- Branch circuit per NEC 310.15—> (3) #12AWG at 75 degree.
- OCPD is given maximum 25A HACR type circuit breaker by the manufacture
- Disconnect per 440.12A1—>1.15x 18.08 = 20.47—> next standard 30A, 3 pole Non-disconnect switch
- EGC per 250.122–> (1) #10AWG