I am reviewing an equipment specification for a large commercial food storage warehouse (Washington State) that has included the following clause
"Provide 120V, 20 amp, weatherproof, duplex GFCI receptacles, factory installed and wired with single point power connection, transformer, power to receptacle ahead of the equipment disconnect." The equipment involved are make-up air units (gas fired and electric coil) and large ventilation fans for emergency smoke evacuation. The equipment manufacturer has indicated this is in violation of NEC and that a separate 115V power source is required for the service receptacles. Can a single point power connection be made to these units?
"Provide 120V, 20 amp, weatherproof, duplex GFCI receptacles, factory installed and wired with single point power connection, transformer, power to receptacle ahead of the equipment disconnect." The equipment involved are make-up air units (gas fired and electric coil) and large ventilation fans for emergency smoke evacuation. The equipment manufacturer has indicated this is in violation of NEC and that a separate 115V power source is required for the service receptacles. Can a single point power connection be made to these units?