Hello guys and gals.
Have a situation where condenser, evaporator, blower, supp. heat, and controls are all located outside in one unit for dwelling. I called hvac company when I roughed in and asked for nameplate info and he said I needed a 100A branch circuit. Now that I am back to finish, I think I might have a situation.
It has two nameplates. One for heat and one for compressor.
Compressor: Min. 16A Max 40A
Heat: Min. 52A Max 65A
It seems to me that I needed 2 circuits. But there is only one terminal block for whole unit. The branch circuit is protected by 100A breaker inside panel.
The 100A is more than both Max ratings, which is a violation.
What am I missing?
Thanks for replies.
Have a situation where condenser, evaporator, blower, supp. heat, and controls are all located outside in one unit for dwelling. I called hvac company when I roughed in and asked for nameplate info and he said I needed a 100A branch circuit. Now that I am back to finish, I think I might have a situation.