HVAC wire size ?

Merry Christmas

Robpaeschke

Member
Location
Washington
Occupation
E
What wire size do I need for a

Electric heat
13.8 kw

Full load amps
60

Minimum circuit ampacity

Circuit 1
27.0

Circuit 2
53

Max overcurrent
Protective Device

Circuit 1
30

Circuit 2
60


Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Sounds like it requires two circuits, one with a minimum conductor size of 53 amps the other a minimum conductor size of 27 amps.

Welcome to the Forum. Please update your occupation in your profile.
 