What is the MCA?Customer has an HVAC unit to be wired. Nameplate say 16.6 FLA with max OCP 25 Amp. HVAC installer says they want us to use #14 and stats it is listed as 20m amp rated. Yes? No? I would use #12 but he iinsist as it is less expensive.
16.6What is the MCA?
The FLA and MCA should be different.16.6
Yes my mistake. compressor is 12.8 and motor is .6. MCA is listed as 16.6The FLA and MCA should be different.
Then #14 is fine since it's rated at 20 amps for this application. It just cannot be NM or UF cable. What is the wiring method?Yes my mistake. compressor is 12.8 and motor is .6. MCA is listed as 16.6
You would also need #12's if using a Liquid Tight whip to the unit.Then #14 is fine since it's rated at 20 amps for this application. It just cannot be NM or UF cable. What is the wiring method?
Explain please. I would have missed this.You would also need #12's if using a Liquid Tight whip to the unit.
60° C rating in wet locations argument?Explain please. I would have missed this.
Yes, Liquidtight in only listed for 60C conductors in wet locations.60° C rating in wet locations argument?
Tell the HVAC guy that you'll handle the electrical and he can stick to the HVAC.Customer has an HVAC unit to be wired. Nameplate say 16.6 FLA with max OCP 25 Amp. HVAC installer says they want us to use #14 and stats it is listed as 20m amp rated. Yes? No? I would use #12 but he insist as it is less expensive.
Nope, all the time, for me.Yes, Liquidtight in only listed for 60C conductors in wet locations.
I'm sure most of us have ignored that limitation a few times.
Agree, since when does the HVAC contractor dictate what size wire to use and why should he care if it's 14 or 12?Tell the HVAC guy that you'll handle the electrical and he can stick to the HVAC.
If the sparky is his sub-contractor then the cost for a #14 circuit vs. #12 is money in the hvac guys pocket. IMO not worth arguing about but some of these guys are really cheap and hey don't want to pay for anything above and beyond the minimum code requirement.Agree, since when does the HVAC contractor dictate what size wire to use and why should he care if it's 14 or 12?
I don't agree. The operational load is 13.4 amps, not 16.6 amps, and that does not exceed the 60°C ampacity of 14 AWG. We do not need to use the MCA for this as that number includes a fictitious 25% increase to the compressor current.You would also need #12's if using a Liquid Tight whip to the unit.
In this case I do agree with you. My post was mainly to bring up that even with 75C conductors the 60C limit would still apply to the Liquidtight. I didn't take the lower MCA of the posted unit into account so even at 60C the #14 are adequate.I don't agree. The operational load is 13.4 amps, not 16.6 amps, and that does not exceed the 60°C ampacity of 14 AWG. We do not need to use the MCA for this as that number includes a fictitious 25% increase to the compressor current.
Seems to me that when the ampacity is required to be 16.6A, you need an installation that could carry 16.6A without violating any temperature limits. An LFNC installation in a wet location with #14 conductors would not meet that standard.I don't agree. The operational load is 13.4 amps, not 16.6 amps, and that does not exceed the 60°C ampacity of 14 AWG. We do not need to use the MCA for this as that number includes a fictitious 25% increase to the compressor current.