Hybrid Copper-Fiber Armored Cable in same raceway with 120V lighting circuit
YouConduit!
Midwest
Electrical Design
Hey all, a few questions regarding hybrid copper-fiber armored cable and how it can be installed with other 120V circuits:
NEC 300.3(C) allows AC and DC conductors of different systems to share the same raceway or enclosure provided that the AC voltage is less than 1000V and the DC voltage is less than 1500V, AND all conductor insulation is rated for (at least) the maximum system voltage.
NEC 770.133(A) allows fiber to share the same cable tray or raceway with conductors less than 1000V.
So...
Can a hybrid copper-fiber armored cable be in the same raceway as a 120V lighting circuit provided that the copper conductors in the hybrid cable have insulation rated at least 120V? The hybrid copper cables and fiber go to a 48VDC load (communications equipment). All loads are on a pole.
Do NEC sections 724/725 apply at all here?
Would innerduct be best practice for this application to keep 120V power and the hybrid cable separate within a larger raceway?
Please let me know your thoughts/experience! Thanks in advance.
Yes, a hybrid copper-fiber armored cable can share a raceway with a 120 V lighting circuit, if all conductors are insulated for the highest voltage present (per NEC 300.3(C)(1)). Since the lighting circuit is 120 V, the copper conductors in the hybrid cable must be rated at least 120 V (typically 300 V or 600 V). The fiber itself is permitted to share the raceway with power conductors under NEC 770.133(A)(1).
I remember seeing this when it was first posted.
Your question is layered.
1) Communication companies, power companies and their rules.
2) NEC
What you are describing is a class 4 circuit or a typical 120V + Fiber for an antenna. The NEC adopted it and so did the NESC a while back. They allow for communication circuits to include what the NEC considers a class 4 circuit.
California has not adopted that for utilities. We use GO95. We have not changed the definition of a communication class circuit.
Yes use innerduct to avoid damaging another companies wire. Especially if you are selling antenna space or if the same company is going to use the wireless to continue backbone circuits. Like ATT or Verizon.
If your working for a phone company they might internal practices that would not allow mixing conduits with power or another carrier.