I just got this question wrong . My answer (b) was based , in part , on what I thought I learned at this forum ,...... so does the external metal pump casing and the metalic water supply need a #8 bond ? I say yes
680.74 Bonding Hydromassage Bathtubs
question id# 0274
Metal piping systems that supply Hydromassage bathtubs must be grounded
Article 680.74 in the 2002 NEC? was changed by deleting wording that required listed double-insulated pumps to provide a ?means for grounding internal, non-accessible, non-current carrying metal parts.? This change was supported by comments that pointed out that the 2002 NEC? language was appropriate for swimming pool pumps which are not-double insulated. Requiring bonding of internal parts of listed double-insulated hydromassage pumps would violate their listing.
The change was unanimously approved because the panel believed that an increased level of safety was provided for these installations when listed double-insulated hydromassage pumps were connected to a power source by means of a three wire cord that included an equipment grounding conductor.
Question 274.
Which of the following components of a hydromassage tub are required to be bonded together by a #8 AWG copper conductor?
A: Internal non-current carrying metal components of a listed double-insulated hydromassage pump
B: Metal piping on the tub that is in contact with circulating water
C: Metal piping that supplies water to the tub
D: Both b & c are correct
previous question
Main Menu
Next question
Choice B is incorrect
(d) is correct. The change in article 680.74 omitted the requirement for bonding internal components of listed double-insulated hydromassage pumps because this would violate the listing of the pump.
Please continue on to the next question. You may review this question by going to the main menu
680.74 Bonding Hydromassage Bathtubs
question id# 0274
Metal piping systems that supply Hydromassage bathtubs must be grounded
Article 680.74 in the 2002 NEC? was changed by deleting wording that required listed double-insulated pumps to provide a ?means for grounding internal, non-accessible, non-current carrying metal parts.? This change was supported by comments that pointed out that the 2002 NEC? language was appropriate for swimming pool pumps which are not-double insulated. Requiring bonding of internal parts of listed double-insulated hydromassage pumps would violate their listing.
The change was unanimously approved because the panel believed that an increased level of safety was provided for these installations when listed double-insulated hydromassage pumps were connected to a power source by means of a three wire cord that included an equipment grounding conductor.
Question 274.
Which of the following components of a hydromassage tub are required to be bonded together by a #8 AWG copper conductor?
A: Internal non-current carrying metal components of a listed double-insulated hydromassage pump
B: Metal piping on the tub that is in contact with circulating water
C: Metal piping that supplies water to the tub
D: Both b & c are correct
previous question
Main Menu
Next question
Choice B is incorrect
(d) is correct. The change in article 680.74 omitted the requirement for bonding internal components of listed double-insulated hydromassage pumps because this would violate the listing of the pump.