Lets say... service lateral.
There's a utility pole.
Conductors come down the pole to a MOCP device mounted on the pole.
The neutral is bonded to the enclosure. There are also two ground rods driven and the grounding electrode conductor from them is connected to the bonded neutral in that enclosure.
The service conductors (feeder) are run underground to a dwelling unit. (phase 1,2,N,egc) In the dwelling, do all grounding electrodes and H2O system now just get connected to the EGC bar only and NOT to the floating neutral?
OR would one have to some how get the dwelling grounding electrode conductor from dwelling to the main out at the pole?
OR would one use two ground rods and ground and bond the neutral at the pole and , then run 3 conductor to the dwelling (no egc) and bond and ground it again using the ground electrodes on premises and additional ground rods?
I'm thinking there would be a egc run from the utility pole and all existing grounding electrodes in the dwelling would go to the equipment ground in the panel.
Wondering... Thank you