Is it possible or practical to protect all lines in a system (power grid) with differential protection only?
It is not possible in all cases. Not all lines have communication over to the other side, hence, power line carrier.
It is also not practical in all cases. For example, radial circuits could not use line diff (LD) principles since there is no source at the other end.
Also, LD is not always the best protection scheme. There are several ways to provide LD protection. I believe all the relay mfrs have their own special way of applying this principle (RFL-Charge Comparison, SEL-Alpha plane, etc.).
Possible? Yes, if you communicate with all endpoints and properly account for losses. I would think do-able for small systems.Is it possible or practical to protect all lines in a system (power grid) with differential protection only?
True. Some type communication system will be in place.How much would it add to capitol costs if all none radial lines were equipped with PLC or OPGW for communication? My understanding (though humble) is that most none radial 115 and 345kv lines have some sort of communication scheme already in place to aid conventional protection such as permissive overreaching transfer trip.
Yes. A net zero state is the target.If you have a CT on the other end (both ends) and communication, would it still not be possible to implement differential protection?
Non-unit type protection for the center breaker?As is any none radial line on a breaker and a half substation requires communication for remote tripping should the center breaker become stuck?
Possible? Yes, if you communicate with all endpoints and properly account for losses. I would think do-able for small systems.
Practical? Very unlikely. You still need other things like overload protection and even state analysis for bigger systems.
Non-unit type protection for the center breaker?
I do not know anything about this. How does it work?
Non unit type of protection includes time graded over current protection;current graded over current protection and distance protection. Such non unit type protections don’t have pilots.
Why do you not consider operation of any upstream breaker, beyond LD protection, in that case?But you would still need communication in the event the middle breaker fails to trip for a fault in breaker and 1/2?
Why do you not consider operation of any upstream breaker, beyond LD protection, in that case?
My understanding is that (though I could be wrong) that differential protection becomes preferred as primary relaying the larger or more complex the system especially at 345kv.
How much would it add to capitol costs if all none radial lines were equipped with PLC or OPGW for communication? My understanding (though humble) is that most none radial 115 and 345kv lines have some sort of communication scheme already in place to aid conventional protection such as permissive overreaching transfer trip.
mbrooke said:These lines would (and do) receive standard 50/51 relays, however, theoretically do you really need a source? If you have a CT on the other end (both ends) and communication, would it still not be possible to implement differential protection?
It is typical but, not mandatory. There are other ways with dealing with Breaker Failure at substations that do not have a Breaker Failure scheme. For example, many utilities use a forward Zone 3 at the remote end that reaches to the end of the adjacent line to monitor the middle breaker. Also, you can use reverse Zone 3 on all the other terminals in the local sub.As is any none radial line on a breaker and a half substation requires communication for remote tripping should the center breaker become stuck?
Also just to add when I say system with just differential protection I am only referring to 500, 345 and 115kv transmission lines. 34.5 sub transmission and 12.47kv distribution lines are operated radially and protected by conventional time over current relays so these are excluded in this thread.
Pilot wire schemes are usually economical only for short distances with the restriction of voltage drop due to impedance of the pilot wires. These in turn cause energy loss.
To overcome the drawbacks of all conventional protection communication schemes used and to maintain high reliability and lowering of energy loss, it is necessary to use accurate communication media like wireless communication protocol between the relays.
Why do you not consider operation of any upstream breaker, beyond LD protection, in that case?
Pilot wire schemes are usually economical only for short distances with the restriction of voltage drop due to impedance of the pilot wires. These in turn cause energy loss.
To overcome the drawbacks of all conventional protection communication schemes used and to maintain high reliability and lowering of energy loss, it is necessary touse accurate communication media like wireless communication protocol between the relays.
OK, now you're starting to confuse protection schemes. You cannot use LD with PLC. So, what's your question....can you use LD everywhere or can you use a pilot scheme everywhere?
You technically can but, it does not offer any faster response than a 50 element or a Zone 1 that reaches the entire line and half way through the xfmrs.
It is typical but, not mandatory. There are other ways with dealing with Breaker Failure at substations that do not have a Breaker Failure scheme. For example, many utilities use a forward Zone 3 at the remote end that reaches to the end of the adjacent line to monitor the middle breaker. Also, you can use reverse Zone 3 on all the other terminals in the local sub.
This clear things up for me as to what you are asking. Where I was getting confused was for most 115kV and some 230kV lines. For me, the problem I have with your philosophy on LD is that many 115kV and 230 kV lines have tapped loads off the line to feed residential, commercial, and industrial loads. The number of taps could be many. This makes it extremely difficult for an LD scheme. A POTT or DCB scheme would work just fine for this.
However, typical 500 and 345kV lines are transmission only where there is only two or three terminals. In these cases, I believe you are completely correct about an LD or some other pilot scheme. I think most utilities have standardized some type of pilot scheme (LD, POTT, DCB, DCUB, etc.) for both the primary and backup line relays.