Can I wire a house with so cord ?
400.8 Uses Not Permitted. Unless specifically permitted
in 400.7, flexible cords and cables shall not be used for the
following:
(1) As a substitute for the fixed wiring of a structure
Can I wire a house with so cord in conduit ?
following:
No
There is also a code section prohibiting cords from conduit.
If I may ask , What is the reason for the question?
400.8(6) specifically mentions raceways, but also says except as otherwise permitted in this code, so there must be some limited cases where it can be in raceway, though I can't think of any.I cannot find that section help please.
SO would normally be more expensive then NM cable anyway so I don't see that great of a desire to use such a method as the main wiring method of the entire dwelling. But you occasionally have those that somehow end up with a bunch of cord or specific use cable and think they can save a lot of money by using it.
That may be one of the "except as otherwise permitted in this code" instances, otherwise as a general rule flexible cord is not permitted in raceways.You can't substitute NM cable with SO cable, but you can use SO cable inside a conduit. Sounds like a big waste of money using SO cable in a conduit instead of THHN or similar wire though.
For swimming pools and fountains, all niche lights have SO cords inside a PVC conduit. I also specify several other types or cords inside PVC conduit, depending on the application.
As a general rule flexible cord IS permitted in a raceway but not all raceways .
following:
(6) Where installed in raceways, except as otherwise permitted
in this Code
If it is a low voltage wiring usually 12v or 24v and not line voltage 110v or 240v wiring, rated wiring may not be required from transformers to outlets.