A single-phase hermetic refrigerant motor compressor has a rated load current of 24 amperes and a branch circuit selection current of 30 amperes. The branch circuit conductors are copper, Type TW. They operate at 80 degrees farenheit, and they are the only conductors in the conduit to this compressor. The smallest possible branch circuit conductors must be at least size ______ AWG.
A. 12
B. 10
C. 8
D. 6
The correct answer, according to the Master's Electrician Review, is C. - is there anyone out there who can explain why it needs to be 125% of the branch circuit if it's already rated at 125% of the motor FLA?
24 x 1.25 = 30, right? Why does it need to go another 25%?
Reference Article 440-32 2005 NEC