I guess this settles the argument. Anyone see any loopholes?
Submitter: Brian J. Dolan, IBEW/NECA Technical Institute
Recommendation: Add the following FPN after 220.14(l):
FPN: The load calculation in 220.14(l) does not limit the number of
receptacles on a single branch circuit.
Substantiation: This section is a perennial topic of misunderstanding, and
deserves clarification. The proposed wording is similar to the FPN following
410.151(B).
Panel Meeting Action: Reject
Panel Statement: The material proposed is not appropriate for a FPN since it
contains an interpretation. In addition, the submitter is incorrect in that
220.14(I) does limit the number of receptacles on a branch circuit for
applications other than dwelling units covered in 220.14(J) and banks and
office buildings covered in 220.14(K).
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
Submitter: Brian J. Dolan, IBEW/NECA Technical Institute
Recommendation: Add the following FPN after 220.14(l):
FPN: The load calculation in 220.14(l) does not limit the number of
receptacles on a single branch circuit.
Substantiation: This section is a perennial topic of misunderstanding, and
deserves clarification. The proposed wording is similar to the FPN following
410.151(B).
Panel Meeting Action: Reject
Panel Statement: The material proposed is not appropriate for a FPN since it
contains an interpretation. In addition, the submitter is incorrect in that
220.14(I) does limit the number of receptacles on a branch circuit for
applications other than dwelling units covered in 220.14(J) and banks and
office buildings covered in 220.14(K).
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12