Elecestim123
Member
- Location
- MN
- Occupation
- Electrical Estimator
Been googling like hell to try to understand. I like to understand how/why things work/are the way they are, and not just do it because you're told to.
So I understand when the 125% rule applies, and how to size a breaker for it and all that. I even get youre sizing the wire/CB larger to overcome the heat problem. My question isn't about trying to understand the rule to apply it, or how to apply it. My question is probably more related to the theory of it.
The general idea of a breaker is to stop the flow of current when there's too much of a current draw. If you have a piece of equipment sized to draw 200A, that's stating it can safely handle UP to 200A. Any more current then that it needs a circuit breaker to stop the flow of current so it doesn't become damaged. I also know for motors there's a large inrush current, and breakers are designed to handle this SHORT burst of inrush current. But with the 125% rule for continuous loads, with the 200A example your breaker is now loaded to 250A. This means if there's a problem and there's say 235A being drawn by the load now, the breaker won't trip, and in the mean time the equipment is being damaged.
Am I completely overthinking this?
Is it as simple as the load can only draw what it draws, so there's no reason it would ever draw over 200A anyways, so there would never be more than that being drawn, and if there's a ground fault/short that would be a huge amount of current anyways so the breaker would trip? I feel like this is the answer, and therefore this is a dumb question, but in case it's not, I'm curious to know the answer.
So I understand when the 125% rule applies, and how to size a breaker for it and all that. I even get youre sizing the wire/CB larger to overcome the heat problem. My question isn't about trying to understand the rule to apply it, or how to apply it. My question is probably more related to the theory of it.
The general idea of a breaker is to stop the flow of current when there's too much of a current draw. If you have a piece of equipment sized to draw 200A, that's stating it can safely handle UP to 200A. Any more current then that it needs a circuit breaker to stop the flow of current so it doesn't become damaged. I also know for motors there's a large inrush current, and breakers are designed to handle this SHORT burst of inrush current. But with the 125% rule for continuous loads, with the 200A example your breaker is now loaded to 250A. This means if there's a problem and there's say 235A being drawn by the load now, the breaker won't trip, and in the mean time the equipment is being damaged.
Am I completely overthinking this?
Is it as simple as the load can only draw what it draws, so there's no reason it would ever draw over 200A anyways, so there would never be more than that being drawn, and if there's a ground fault/short that would be a huge amount of current anyways so the breaker would trip? I feel like this is the answer, and therefore this is a dumb question, but in case it's not, I'm curious to know the answer.