D darrdean Member Location Beachwood, Ohio Occupation Electrician Sep 28, 2021 #1 I have a circuit that is in life safety and needs moved to life critical. Does the conduit need to dedicated for life critical and removed from life safety?
I have a circuit that is in life safety and needs moved to life critical. Does the conduit need to dedicated for life critical and removed from life safety?
D d0nut Senior Member Location Omaha, NE Sep 28, 2021 #2 Yes. The life safety branch and critical branch need to be kept entirely separate from all other branches. See 517.31(C)(1).
Yes. The life safety branch and critical branch need to be kept entirely separate from all other branches. See 517.31(C)(1).