I have a circuit that is in life safety and needs moved to life critical.

Status
Not open for further replies.

darrdean

Member
Location
Beachwood, Ohio
Occupation
Electrician
I have a circuit that is in life safety and needs moved to life critical. Does the conduit need to dedicated for life critical and removed from life safety?
 

d0nut

Senior Member
Location
Omaha, NE
Yes. The life safety branch and critical branch need to be kept entirely separate from all other branches. See 517.31(C)(1).
 